IanT599



Member Since: 15 Jun 2013
Location: Wellington
Posts: 351

United Kingdom 
Domestic house electrics

Hi all,

Currently rewiring the house at present but need a little advice.

Currently have the main consumer unit inside the house feeding the house as expected. There is a 6mm cable on a 32A mcb feeding the garage consumer unit which has sockets, lights and the old shower circuit.

Now the garage unit has a 100A main switch and an RCD for the sockets, lights etc.
The starting 32A mcb in the main consumer unit isn't RCD protected and goes to the garage consumer unit.

Now as part of the rewire I'm not sure exactly how to proceed on the here.

My garage consumer unit will be getting renewed and have 2 additional circuits. 16A to supply the caravan and a 30A for a welder connection. TBH probably only need 16A for the welder but probably better to over spec just in case.
Now the welder I'm sure would require a 32A type C RCBO with 6mm cable as in trunking/conduit fed from the 100A main switch as an independent circuit.
The rest of the garage would be on the 80A 30mA RCD with individual mcb.

I'd imagine I'd need 16mm cable to feed the garage consumer unit through the ceiling vid through joists.

The question really is what do I feed the garage with from the main consumer unit?
Is it ok to have a 100A main switch on the garage consumer unit even though at present it is fed by a 32A mcb?

Originally thought about splitting the tails but the garage unit is about 10m away from the incoming mains and the consumer unit.

Any thing that is over spec or under spec let my know please.

Thanks
Ian

Post #386971 13th May 2016 10:31pm
View user's profile Send private message View poster's gallery Reply with quote
p38arover



Member Since: 16 Dec 2015
Location: Western Sydney
Posts: 1536

Australia 

You're allowed to do your own electrics? Shocked Ron B. VK2OTC
2003 L322 V8 Auto
2007 Yamaha XJR1300
Previous: 1983, 1986 RRC; 1995, 1996 P38A; 1995 Disco1; 1984 V8 County 110; Series IIA

Post #386978 14th May 2016 1:06am
View user's profile Send private message View poster's gallery Reply with quote
mzplcg



Member Since: 26 May 2010
Location: Warwickshire. England. The Commonwealth.
Posts: 4029

United Kingdom 2014 Range Rover Vogue SE SDV8 Corris Grey

The basic rules regarding MCBs, breakers, cable thicknesses etc is simple.

1 The breaker protecting a ciruict should never exceed the maximum rating for the infrastructure it protects. In other words, the 32a breaker for the garage is fine. Nothing downstream of this can ever exceed 32a total combined load so having a 100a main breaker is OK, although less than ideal. I would take it down as close to 30a as I could get, currently 40a I think.

2 MCBs look for current leaking out of the appliance, i.e. the difference between input to the appliance via LIVE and output from it via NEUTRAL. If this difference exceeds 30 milliamps (soon to be 20) it will trip. This is a very good thing. So, if your 32a feed from the main board is on the non-MCB side you should protect the appropriate circuits on the garage board with an MCB. The welder is not one of those BTW but every 13a socket definitely IS something to protect.

3 Cable gauges are all listed in the online version of 17th edition regs. You would do well to read these regs in depth. Whilst you can argue under Part P that you are a competent person, you would also (if needed) be asked to demonstrate an understanding of the 17th edition.

Aside from the above, assuming you're replacing the garage CU yourself, if it were me I would lay all new wiring and boxes, get it tested by a qualified Sparkie (which I was before 17th came out) and I would connect the new CU to the main incoming supply with 15mm cross section minimum on a 100a main breaker. I would definitely not connect it to the house CU. Just my 2p.

There are cable size calculators on supplier site such as TLC direct. RS components etc.

Post #386993 14th May 2016 7:05am
View user's profile Send private message View poster's gallery Reply with quote
Alistair



Member Since: 11 Feb 2011
Location: Peterborough / Bordeaux / Andorra
Posts: 7946

United Kingdom 2013 Range Rover Vogue SE SDV8 Santorini Black

p38arover wrote:
You're allowed to do your own electrics? Shocked


You can run the cables & connect them up, but everything must be inspected, tested and certified by a qualified electrician before the final connection & operation.

I agree with the above - a breaker has 2 functions - its a switch that allows you to isolate a circuit - and it's also a 'fuse' to prevent excessive current being drawn. So the 100A would just act as a switch - and the 32A one would still be acting as the 'fuse'.

Post #387000 14th May 2016 7:33am
View user's profile Send private message View poster's gallery Reply with quote
Paul J.



Member Since: 13 Jan 2009
Location: Leafy Cheshire
Posts: 279

England 

The 100A main switch is not an automatic circuit breaker (I.e. It will not 'trip' on over current in the same way that a MCB would). The 100A rating simply refers to the maximum current that it will pass safely. If you pass more than the maximum rated current, there is a risk of a resistive heating fault occurring.

In the OP's present situation, the supply to the 100A main switch is restricted to what the upstream 32A MCB can supply without tripping.

Post #387023 14th May 2016 9:06am
View user's profile Send private message View poster's gallery Reply with quote
Alistair



Member Since: 11 Feb 2011
Location: Peterborough / Bordeaux / Andorra
Posts: 7946

United Kingdom 2013 Range Rover Vogue SE SDV8 Santorini Black

Yep - you are correct - I need to wake up before posting - it's only a switch, so makes no difference Thumbs Up

Post #387037 14th May 2016 9:54am
View user's profile Send private message View poster's gallery Reply with quote
axle



Member Since: 28 Oct 2007
Location: Perth Perth the end of the Earth
Posts: 2964

Australia 2008 Range Rover Supercharged 4.2 SC V8 Rimini Red

p38arover wrote:
You're allowed to do your own electrics? Shocked


It's only house bashing and he seems to have a good grasp of whats required , and it will have to be tested and a certificate issued by a qualified sparky . Australia's attitude of not letting you change a plug is all to do with union job protectionism masquerading as safety.

The UK's requirements of wiring are much safer than Australia's yet the attitude to work is a bit more relaxed , funny that Wink 2008 MY Supercharged
Rimini Red / Jet
four zone climate
remote park heater
and no ugly kid windows.
magnus satis quod turpis satis

Post #387055 14th May 2016 11:52am
View user's profile Send private message View poster's gallery Reply with quote
IanT599



Member Since: 15 Jun 2013
Location: Wellington
Posts: 351

United Kingdom 

Sorry should have mentioned I am Part P, 17th edition and I&T qualified.
Although going back 5 years when I became qualified but I decided to go down the gas and plumbing path instead so never joined NICEIC etc to get self certified.

So I'm thinking a 50A RCBO type C in the main consumer unit to feed 16mm cable to the garage consumer unit.

Post #387067 14th May 2016 1:11pm
View user's profile Send private message View poster's gallery Reply with quote
mzplcg



Member Since: 26 May 2010
Location: Warwickshire. England. The Commonwealth.
Posts: 4029

United Kingdom 2014 Range Rover Vogue SE SDV8 Corris Grey

I'd still run it direct from the incoming supply.

BTW, which side of the board is the 32a breaker you intend using? You would't want that on the RCD side if you plan on using a welder.

Post #387098 14th May 2016 3:33pm
View user's profile Send private message View poster's gallery Reply with quote
IanT599



Member Since: 15 Jun 2013
Location: Wellington
Posts: 351

United Kingdom 

I'm sure there are rules on how long meter tails are allowed to be and the garage is 10-15m from the meter.

32A type c rcbo will be on an independent circuit on the garage consumer unit. So not connected to the rcd for the lights and sockets.

Post #387130 14th May 2016 6:40pm
View user's profile Send private message View poster's gallery Reply with quote
mzplcg



Member Since: 26 May 2010
Location: Warwickshire. England. The Commonwealth.
Posts: 4029

United Kingdom 2014 Range Rover Vogue SE SDV8 Corris Grey

Nope, although 2 metres is the norm the stipulation is that when over 3 metres you just have to go up one cable gauge. my meter tails are 14 metres and all signed off OK. I just had to go to 35mm from 25mm when I moved the CU during the house extension.

Post #387132 14th May 2016 7:07pm
View user's profile Send private message View poster's gallery Reply with quote
northernmonkeyjones



Member Since: 24 Mar 2012
Location: derby
Posts: 8620

United Kingdom 2016 Range Rover Autobiography SDV8 Santorini Black

I should think that 16mm would be more than adequate for the garage. 10mm would be sufficient, especially if you are keeping the 32a mcb in the main board to feed the garage.

Personally i wold set it up:

45A breaker in the house board feeding to the garage board
10mm twin and earth to the garage or 10mm underground if separate.

board in the garage with:
5A lighting with 1.0mm cable
16A caravan feed with 2.5mm t&e
16A welder feed with 6mm cable then if you find you need to put a larger breaker in you can
16A sockets feed to a 2.5mm radial circuit.
30ma RCD
100A main switch.

The 45A breaker in the main board will protect the 10mm cable from the house and diversity says you won't draw 45A at any point.

The RCD in the garage board will protect the circuits in there even if you have the MCB in the house board on the non RCD side. Thumbs Up

Remember though that you probably only have 100A or 80A in the main fuse to the house.

usually where welders are involved a 3 phase supply is best as they can draw high currents, but if yours is more domestic and works off a plug then you should be fine. There is nothing that can't be fixed with a hammer😜😜
FFRR 4.4 SDV8 Autobiography Santorini Black.
KIA E-Niro 4+
2010 LR D4 Commercial 2.7 TDV6

Post #387563 17th May 2016 5:42pm
View user's profile Send private message View poster's gallery Reply with quote
Realist



Member Since: 13 Feb 2016
Location: Wales
Posts: 436

Wales 

I would first look at the cable run in total, how its going to be protected, armoured, trunking, conduit or clipped, also is the garage fixed to the house or a separate building? Range Rover quotes.....

The Luxury That�s More Than a Luxury.
Conquer the world, and look good doing it.
Built for the unexpected.
Over prepared, but never underdressed.

2007 Vogue SE TDV8 Epsom Green (old car).
2010 Discovery 3.0L GS Mk4 Black.

Post #387598 17th May 2016 8:41pm
View user's profile Send private message View poster's gallery Reply with quote
IanT599



Member Since: 15 Jun 2013
Location: Wellington
Posts: 351

United Kingdom 

Cable run is approx 8-10metres.

I've thought of running a 10mm cable direct form the main consumer unit to the welder. Running through joists and clipped to them to the attached garage. Last 2m in conduit.
Got a 32A socket for it for the garage. Worst case is if the welder I get is 16A or smaller then change to socket as required.
Got a 40A type c rcbo for it for the main consumer unit. 10mm cable is rated as 63A clipped and 52A in conduit so more than sufficient.

Going to run a second 10mm cable direct clipped and through joist but no conduit to the garage consumer unit.
RCBO type b 50A on the main unit feeding the garage unit.

Got a 16A socket for the caravan to fit too now as arrived.

Post #387615 17th May 2016 9:51pm
View user's profile Send private message View poster's gallery Reply with quote
Realist



Member Since: 13 Feb 2016
Location: Wales
Posts: 436

Wales 

Reply when I'm not so srunk Smile Range Rover quotes.....

The Luxury That�s More Than a Luxury.
Conquer the world, and look good doing it.
Built for the unexpected.
Over prepared, but never underdressed.

2007 Vogue SE TDV8 Epsom Green (old car).
2010 Discovery 3.0L GS Mk4 Black.

Post #387762 18th May 2016 9:32pm
View user's profile Send private message View poster's gallery Reply with quote
Post Reply  Back to top
Page 1 of 2 12>
All times are GMT

Jump to  
Previous Topic | Next Topic >
Posting Rules
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum



Site Copyright © 2006-2025 Futuranet Ltd & Martin Lewis
fullfatrr.com RSS Feed - All Forums


Switch to Mobile site